1920 * 160

TECH - ARCHIVES

Category

OPEN Close

Search posts
[Freezer, Chiller control panel] How to setup temperature and defrost heater?- UCC-MT23
First Egpis Hits:2875 49.150.245.28
2019-08-26 19:46:44

 

Detailed setting

Press the setup button for more than 5 seconds to display the first menu of detailed settings (A-1) in the current temperature window.

Change the setting value using the down or up button.

In this way, if you finish setting up the last menu "dps" and press the last setting button, "SAU" will blink 3 times and the setting will be completed.

Function

Display

Initial value

Range

Temperature deviation

A-1

2℃

1℃ ~ 10℃

Comp delay

A-2

60 Sec.

0 ~ 240 Sec.

Comp Block

A-3

0

0:Not used

(Fixed)

Defrost cycle

A-4

204 Min.

0 ~ 999 Min.

Defrost time

A-5

30 Min.

0 ~ 30 MIn.

EVA fan delay

A-6

10 Sec.

0 ~ 60 Sec.

EVA fan function

A-7

F.1

F.1 ~ F.4

Temperature Compensation

A-8

0℃

-10℃ ~ 10℃

Constant temperature function

A-9

0℃

0℃ ~ 10℃

EVA fan delay after defrost

A-A

0 Sec.

0 ~ 600 Sec.

Comp delay after defrost

A-b

0 Sec.

0 ~ 600 Sec.

Comp operation during defrost

A-c

OFF

ON/OFF

Temperature display after defrost

A-d

On

ON/OFF

Comp accumulated time

A-E

Off

OFF

Buzzer in case of error

Erb

On

On/Off

Abnormal temperature delay time

Ert

0

0: Not used

10 ~ 25 Min.

Abnormal temperature high

temperature deviation

ErH

10℃

1 ~ 10℃

Abnormal Temperature Low

Temperature Deviation

ErL

-5℃

-1 ~ -10℃

Operation mode

dPS

S

Not used/Fix

 

Error message

Display

Error Details

Treatment method

E-1

Temperature

sensor

disconnection

Sensor terminal connection status

Sensor resistance value check

Check electric leak on sensor

E-2

Temperature

sensor

short circuit

Sensor terminal connection check

Breaking off sensor wire

Check electric leak on sensor

Err-dp

DPS Behavior

DSP Behavior:High pressure switch

operation

DP Switch:High Pressure B Contact

Behavior

Err-ocr

Comp. OCR

Behavior

Comp magnet OCR Behavior: Comp capacity, OCR(Settle) Check